Hi All, sorry if this has been touched on before but my Benimar Mileo came supplied with a black ehu lead, I have read that 'orange' are recommended but is it acceptable to use what came with the unit or would it be frowned upon?

Like everyone else, we have been 'grounded' but we had trips booked prior to lockdown & can now pick up our planned trip from the 4th July which will be our 'maiden voyage' as the only trip we have had is collecting it from the dealership after purchase.....

Hopefully, we get some socially distancing help if we are seen struggling.....

Thanks

Paul (Kasspa)

no one replied on 19/06/2020 19:06

Posted on 19/06/2020 19:06

The greater the square area of the conductor the less resistance to electron flow, so the volt drop is less, the cable tends to remain  cooler ie resistance =heat, running a 16amp rated cable (1.5mm2) on a 16 amp supply leaves nothing for wear and tear, aging  etc it would only take a failing toaster element (for instance) and a slow mains breaker to turn the cable into an instant burning fuse (seen it happen on work sites) 1.5mm2 would be ok on a 10A supply but why take the risk on a 16Amp supply.

if you think about it, if I have an appliance that draws exactly 5 amps when on and I fit a 5 amp fuse, the fuse will blow every time I start the appliance as starting current is 8x running current (generally) so i fit a 7 or 10 amp fuse, the appliance will work until a fault occurs.

so i have a 16amp supply I turn stuff on because its winter my electric heater cuts in and draws an overload for a short period but not enough to trip the breaker, the supply cable will be under stress and heat up(even worse if its coiled), the more stress and over time it will fail as it is working at maximum or more of rated capacity.

1.5mm2 may be ok until a 240v fault occurs my advice is to stay safe go big ie 2.5mm2.

 

hitchglitch replied on 19/06/2020 19:51

Posted on 19/06/2020 19:06 by no one

The greater the square area of the conductor the less resistance to electron flow, so the volt drop is less, the cable tends to remain  cooler ie resistance =heat, running a 16amp rated cable (1.5mm2) on a 16 amp supply leaves nothing for wear and tear, aging  etc it would only take a failing toaster element (for instance) and a slow mains breaker to turn the cable into an instant burning fuse (seen it happen on work sites) 1.5mm2 would be ok on a 10A supply but why take the risk on a 16Amp supply.

if you think about it, if I have an appliance that draws exactly 5 amps when on and I fit a 5 amp fuse, the fuse will blow every time I start the appliance as starting current is 8x running current (generally) so i fit a 7 or 10 amp fuse, the appliance will work until a fault occurs.

so i have a 16amp supply I turn stuff on because its winter my electric heater cuts in and draws an overload for a short period but not enough to trip the breaker, the supply cable will be under stress and heat up(even worse if its coiled), the more stress and over time it will fail as it is working at maximum or more of rated capacity.

1.5mm2 may be ok until a 240v fault occurs my advice is to stay safe go big ie 2.5mm2.

 

Posted on 19/06/2020 19:51

A 5 amp fuse will not blow with current inrush at start up because it is designed not to do so. It takes a very long time for a fuse to blow at just over it’s rating. The fuse is there to protect the cable and should be chosen accordingly.

An uncoiled 1.5mm2 cable will carry at least 20 amps outdoors if not coiled (and that’s in a 30 deg. C ambient).  The protective device in the bollard will protect against a continual small overload and short circuit.

As I said, a 2.5mm2 cable is better as it is more robust, however, if you travel on the continent you will see extensive use of 1.5mm2 cable and although there are mainly smaller current rated supplies, 16 amp is available in some areas.

Lutz replied on 19/06/2020 21:00

Posted on 17/06/2020 20:16 by Tigi

Only Brits have orange leads. nobody else seems to worry.

Posted on 19/06/2020 21:00

That's right. I've never seen an orange lead outside the UK.

Mine's yellow, by the way, not orange.

near Malvern Hills Club Campsite Member photo by Andrew Cole

Book a late escape

There's still availability at many popular UK Club campsites - find your perfect pitch today for a last minute trip!

Book now
Woman sitting in camping chair by Wastwater in the Lake District with her two dogs and picnic blanket

Follow us on Facebook

Follow the Caravan and Motorhome Club via our official Facebook page for latest news, holiday ideas, events, activities and special offers.

Photo of Wast Water, Lake District by Sue Peace
Visit Facebook